You said 2 sets of 3/0 you will need to go to Table 8 Conductor Properties to find the area of 3/0s and multiply that by 2 to find the equivalent area for your set up.Size of Largest Ungrounded Service-Entrance Conductor or Equivalent Area for Parallel Conductors (AWG/kcmil)
To the rods all you are required to use is 6 AWG regardless of the service conductor size.Originally posted by djtazjr:
It will be terminated on 8'x5/8" ground rods.