I installing a 60 amp sub-feed for a sales trailor. I up sized the feeders to # 2 alum for voltage drop. Do I size the ground according to the wire size or breaker size? wire size would # 8 and breaker size would be # 10. I am using a copper bond.
By upsizing the ungrounded from #8 to #2, the EGC must also be upsized in proportionately according to circular mils as shown in Table 8 of the NEC and as required per 250.122(B).