250.66 Size of Alternating-Current Grounding Electrode Conductor
The size of the grounding electrode conductor at the service, at each building or structure where supplied by a feeder(s) or branch circuit(s), or at a separately derived system of a grounded or ungrounded ac system shall not be less than given in Table 250.66, except as permitted in 250.66(A) through (C).
(A) thru ( c) are electrodes with max sizing.
350 MCM conductor for laterals - grd rod to MDP 6#CU, UFER to MDP 4#CU, Water pipe to MDP 1/0 CU -- grd rod to UFER 6# CU, UFER to WP 4# CU, WP to mdp 1/0 CU -- WP to UFER 1/0 CU, UFER to grd rod 1/0 CU, grd rod to MDP 1/0 CU you cannot reduce the size of an electrode condcutor if run in series with other electrodes. Min size for the specific eletrode applys to the specific electrode only.
