We have a 3 Phase 120/208 320 amp meter socket. With (2) 3/0 cu conductors per phase. Feeding (2) 200 amp Main breaker Panels. (1) conductor from each phase terminating at each of the 200 amp Main breakers. Technically NOT a parallel connection because only one side of the conductors are terminated at the same point. Would the size be based on the largest Ungrounded conductor 250-66 and 255-102 (c)(1) in this case 3/0. Requiring (2) # 4 cu OR treat the installation like a parallel connection requiring (1) 1/0