espinoza569
Member
- Location
- San Diego
In class we were discussing the sizing of conductors feeding a motor. In the example, the FLC was figured out to be 23 amps using THWN wire. Then going to 310.15 (B)(16) #12 THWN is rated for 25 Amps. However, the ** refers you to 240.4(D) which states "small conductors" such as 12AWG will be rated for 20 AMPS. The instructor says based on this, you have to run 10 AWG.
I think you can still use 12AWG. According to 240.4(D) - "Unless specifically permitted in 240.4(E) or (G)....." continue to the next page in section (G) - "Over current Protection for Specific Conductor Applications"....Motors is in that "specific application". I argue that because it falls into this category, 240.4(D) does not apply which will allow you to use the full ampacity of 12AWG according to 310.15 (B)(16).
I think you can still use 12AWG. According to 240.4(D) - "Unless specifically permitted in 240.4(E) or (G)....." continue to the next page in section (G) - "Over current Protection for Specific Conductor Applications"....Motors is in that "specific application". I argue that because it falls into this category, 240.4(D) does not apply which will allow you to use the full ampacity of 12AWG according to 310.15 (B)(16).