size of neutral wire

Status
Not open for further replies.

Smart $

Esteemed Member
Location
Ohio
when the neutral wire carry no current like in 4-wire multi-wire with equal load
what size we install?
As Rob said...

You have to consider the neutral current under all operating conditions. Say you had 16A lighting load on each line. Switch all but one line off. The neutral current would now be 16A.
 