Size of overhead wire

Status
Not open for further replies.

SAP

Senior Member
Location
Fresno Ca
Back feeding 50 amp solar breaker residential, installing new 125 amp busing with 100 amp main service disconnect, overhead service. I'm using #4 AWG for my overhead conductors I size my conductors off of my 100 amp MSD, or should I be using #2
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Per table 310.15(B)(7) you can use 4awg if it's a residential single phase service. The language is changing in the new code next month but I think the answer in this case is still the same.

EDIT: that's as long as you're not in a jurisdiction that requires the service conductors to match the bussing instead of the breaker. But that's usually a utility thing, and not required by PG&E.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
EDIT: that's as long as you're not in a jurisdiction that requires the service conductors to match the bussing instead of the breaker. But that's usually a utility thing, and not required by PG&E.
The only POCO I have heard of the requires service size to match "nominal" size of main (service disconnect) panel rather than main breaker size is Los Angeles DWP.
It makes it really hard to meet 120% rule by upsizing the panel only and using a small main breaker to match the service. :)

Sent from my XT1585 using Tapatalk
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
The only POCO I have heard of the requires service size to match "nominal" size of main (service disconnect) panel rather than main breaker size is Los Angeles DWP.
It makes it really hard to meet 120% rule by upsizing the panel only and using a small main breaker to match the service. :)

Palo Alto, too.
 