Oldmaster2

Member
Location
PA
Occupation
Master Electrician
A client of mine had a home inspection and the 100 amp service cable had to be replaced. Inspector informed me that 2/2/4 -al. is no longer legal. Anybody else run into this?
 

Oldmaster2

Member
Location
PA
Occupation
Master Electrician
It does. He is a city electrical inspector. This particular install has a 100 amp panel and a sub-panel. He commented that #1 SEU is not made so you need to install conduit?
 
As long as the #2 is serving the entire load of a single dwelling unit, you can use for a 100A service. I have no idea what this inspector is talking about, unless maybe like letgomywago said, he's not familiar with the revision that added the 83% wording instead of the table.
 

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
It does. He is a city electrical inspector. This particular install has a 100 amp panel and a sub-panel. He commented that #1 SEU is not made so you need to install conduit?
1 is made

Does your local area not allow seu by local amendment
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It does. He is a city electrical inspector. This particular install has a 100 amp panel and a sub-panel. He commented that #1 SEU is not made so you need to install conduit?
Even if they didn't make #1 Al SEU you could always use a larger size SE cable. Sounds like the inspector is incorrect on this one.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
This particular install has a 100 amp panel and a sub-panel.
So for a single dwelling unit, you have:

#2 Al service conductors -- 100A service OCPD -- 100A bus with other OCPD -- 100A feeder OCPD -- #2 Al feeder conductors

If so, that's fine, in this case the 83% rule applies to both the service conductors and the feeder conductors. It would make little sense to require the feeder conductors to be physically larger than the service conductors.

Cheers, Wayne
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
So for a single dwelling unit, you have:

#2 Al service conductors -- 100A service OCPD -- 100A bus with other OCPD -- 100A feeder OCPD -- #2 Al feeder conductors

If so, that's fine, in this case the 83% rule applies to both the service conductors and the feeder conductors. It would make little sense to require the feeder conductors to be physically larger than the service conductors.

Cheers, Wayne
Correct, but many code users get hung up on the requirement that the feeder must carry 100% of the dwelling unit load and do not read 310.15(B)(7)(3) which permits the use of the smaller conductor for a feeder even where the feeder does not carry 100% of the dwelling unit load.
(3) In no case shall a feeder for an individual dwelling unit be required to have an ampacity greater than that specified in 310.15(B)(7)(1) or (2).
 