A client of mine had a home inspection and the 100 amp service cable had to be replaced. Inspector informed me that 2/2/4 -al. is no longer legal. Anybody else run into this?
He doesn't know about the 83% rule for residential.A client of mine had a home inspection and the 100 amp service cable had to be replaced. Inspector informed me that 2/2/4 -al. is no longer legal. Anybody else run into this?
Another inspector who needs a new line of work - sorry but its just not working out.A client of mine had a home inspection and the 100 amp service cable had to be replaced. Inspector informed me that 2/2/4 -al. is no longer legal. Anybody else run into this?
I have a feeling it's a home inspector which is imaginary authorityAnother inspector who needs a new line of work - sorry but its just not working out.
1 is madeIt does. He is a city electrical inspector. This particular install has a 100 amp panel and a sub-panel. He commented that #1 SEU is not made so you need to install conduit?
Even if they didn't make #1 Al SEU you could always use a larger size SE cable. Sounds like the inspector is incorrect on this one.It does. He is a city electrical inspector. This particular install has a 100 amp panel and a sub-panel. He commented that #1 SEU is not made so you need to install conduit?
So for a single dwelling unit, you have:This particular install has a 100 amp panel and a sub-panel.
Yes the table is back as Table 310.12 in the 2020 code. It can also be found in Example D7 in Annex D in the 2017 code.Didn't the table come back in 2020? (We're still on the 2017 code.)
Correct, but many code users get hung up on the requirement that the feeder must carry 100% of the dwelling unit load and do not read 310.15(B)(7)(3) which permits the use of the smaller conductor for a feeder even where the feeder does not carry 100% of the dwelling unit load.So for a single dwelling unit, you have:
#2 Al service conductors -- 100A service OCPD -- 100A bus with other OCPD -- 100A feeder OCPD -- #2 Al feeder conductors
If so, that's fine, in this case the 83% rule applies to both the service conductors and the feeder conductors. It would make little sense to require the feeder conductors to be physically larger than the service conductors.
Cheers, Wayne
(3) In no case shall a feeder for an individual dwelling unit be required to have an ampacity greater than that specified in 310.15(B)(7)(1) or (2).