Size of SEU
Oldmaster2
PA
Master Electrician
A client of mine had a home inspection and the 100 amp service cable had to be replaced. Inspector informed me that 2/2/4 -al. is no longer legal. Anybody else run into this?
It does. He is a city electrical inspector. This particular install has a 100 amp panel and a sub-panel. He commented that #1 SEU is not made so you need to install conduit?
As long as the #2 is serving the entire load of a single dwelling unit, you can use for a 100A service. I have no idea what this inspector is talking about, unless maybe like letgomywago said, he's not familiar with the revision that added the 83% wording instead of the table.
1 is made
Does your local area not allow seu by local amendment
Even if they didn't make #1 Al SEU you could always use a larger size SE cable. Sounds like the inspector is incorrect on this one.
So for a single dwelling unit, you have:
#2 Al service conductors -- 100A service OCPD -- 100A bus with other OCPD -- 100A feeder OCPD -- #2 Al feeder conductors
If so, that's fine, in this case the 83% rule applies to both the service conductors and the feeder conductors. It would make little sense to require the feeder conductors to be physically larger than the service conductors.
Cheers, Wayne
Cheers, Wayne
Correct, but many code users get hung up on the requirement that the feeder must carry 100% of the dwelling unit load and do not read 310.15(B)(7)(3) which permits the use of the smaller conductor for a feeder even where the feeder does not carry 100% of the dwelling unit load.
(3) In no case shall a feeder for an individual dwelling unit be required to have an ampacity greater than that specified in 310.15(B)(7)(1) or (2).