I've been looking, to no avail, to find a chart that lists the strand size in stranded cable, from 8ga to 500MCM. All mfg list count but I dont see a size. Would the strands be a standard size?
For example, southwire 250 to 500MCM all has 37 strands. What size would they be tho? There are 5 cables in that range (250, 300, 350, 400 and 500MCM) - would they be made of 37 10,11,12,13,14ga, metric sizes???
Also, 500MCM is good for 430A at 90C. Assuming the strands are 10ga wire, why is there such a severe derating over 37 separate 10ga wires? If you had 37 10ga CCC in a conduit, you'd be at 40% derating. 37 x 40 = 1480 x .4 = 592A.
eta: no sooner I post this thread Ifound a chart that lists strand size:
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet46***
37 116 mil wires. By this chart:
http://www.engineeringtoolbox.com/awg-wire-gauge-circular-mils-d_819.html
that puts it larger than #10, yes?
*** where are those ampacities coming from?
For example, southwire 250 to 500MCM all has 37 strands. What size would they be tho? There are 5 cables in that range (250, 300, 350, 400 and 500MCM) - would they be made of 37 10,11,12,13,14ga, metric sizes???
Also, 500MCM is good for 430A at 90C. Assuming the strands are 10ga wire, why is there such a severe derating over 37 separate 10ga wires? If you had 37 10ga CCC in a conduit, you'd be at 40% derating. 37 x 40 = 1480 x .4 = 592A.
eta: no sooner I post this thread Ifound a chart that lists strand size:
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet46***
37 116 mil wires. By this chart:
http://www.engineeringtoolbox.com/awg-wire-gauge-circular-mils-d_819.html
that puts it larger than #10, yes?
*** where are those ampacities coming from?