zemingduan
Senior Member
- Location
- Philadelphia,PA
- Occupation
- Electrical Designer
Let's say you have a high rise building and the incoming electrical service of the building is 480Y/277V 3ph 4wire. You will need a 480V 3ph 3wire - 208Y/120V 3ph 4wire transformer to supply (30) Apt. units on 10th & 11th floors. The NEC calculated load for these (30) Apt. units is 327 KVA based on NEC 220.84.
1. Are you allowed to use a 300 KVA transformer for the (30) Apt. Units by NEC? My thought is yes, since I think NEC Article 450 doesn't require you to size the transformer for these Apt. based on 220.84.
2. Will you specify 300KVA transformer for this case? The next standard transformer is 500KVA which is overkill for the (30) Apt. units. In practical, the actual KVA demand maybe just around 0.4-0.5 of the NEC calculated load. 300 KVA transformer should be enough. But as an engineer, is it good to specify 300 KVA for this case?
Let me know you thoughts fellows! Thanks!
1. Are you allowed to use a 300 KVA transformer for the (30) Apt. Units by NEC? My thought is yes, since I think NEC Article 450 doesn't require you to size the transformer for these Apt. based on 220.84.
2. Will you specify 300KVA transformer for this case? The next standard transformer is 500KVA which is overkill for the (30) Apt. units. In practical, the actual KVA demand maybe just around 0.4-0.5 of the NEC calculated load. 300 KVA transformer should be enough. But as an engineer, is it good to specify 300 KVA for this case?
Let me know you thoughts fellows! Thanks!