Re: size wire for 245 amp 480v machine
thanx u guys; i did make a mistake with the 250 mcm, and i agree with 2/0 seeing that the motors do not start all at once. it's a sequenced start. so u guys are great. ground, i was thinking no. 3. now, here's something to discuss. this is not the first machine of this type to be installed in the plant. the first 2 were before my time. they put 600 mcm on the machines which is way overkill. additional this type of sander, the conveyor bed is fixed and the whole machine moves up and down depending on the thickness of the wood doors it's sanding. their solution was to run 3' emt to the machine and use flex the last 3 ft. they're using thhn for the conductor. i'm not comfortable with this. i had considered using 2/0 welding cable but i don't think the insulation thicknes will be code. the ultimate solution is to hard pipe to a crouse-hinds non-fusible pin/sleeve disconnect , and make up a pin and sleeve pigtail using 2/0 sjo. however nobody makes a pin and sleeve over 200 amps, and i'm not sure i need that big of connector type system, seeing that the machine does not suck up 245 amps on start up. what do u think -bj