I am not confident with this wire size. I need some help here please to understand
The system goes from main breaker —> local disconnect switch —->VFD —-> motor
The motor nameplate is 460V, 40HP, 3P. S.f 1.15, FLA, 45A
Table 430.250 gives us 40HP- FLC is 52A
Overload protection - VFD ACH580-01 matching the motor HP and voltage
430.22 - 125% of FLC = 65A——-> 3#4AWG
430.52 branch overcurrent protection
175% of FLC = 91A ~ 90A
Question is motor branch overcurrent protection size per motor is 90A fuse.
The VFD manufacturer protection is required 80A fuse maximum. Do I go with 80A?
main breaker(80A) --3#4 and 1#8G to local disconnect switch (80A fuse) —->VFD to motor 3#4 shield cable
Am I missing something?