I have 400A panelboard with CALCULATED DEMAND amps of 30amps at this time.
The feeder breaker to the panelboard is 400A while the engineer has provided feeder cable size to panelboard of #10awg copper.
I let the engineer know this is not correct as the cable size has to be 500kcmil copper but engineer argues that demand load right now is 30 amps so #10awg copper is correct.
Is the engineer correct or incorrect?
The feeder breaker to the panelboard is 400A while the engineer has provided feeder cable size to panelboard of #10awg copper.
I let the engineer know this is not correct as the cable size has to be 500kcmil copper but engineer argues that demand load right now is 30 amps so #10awg copper is correct.
Is the engineer correct or incorrect?