P.E.S. said:I need help to size a water/gas bonding conductor on a 600 a service. There are no feeder conductors for me to know the size. Inspector calling for
#3/0cu, that seeems too big, but cannot find specifically in code to refute or agree with his call. Thanks!
I contacted Power company, to see what size feeders they were going to pull to new 600a service. going to pull parallel 350kcmil. Inspector said cannot go on size of feeders because they are not installed yet. Hope that helped clarify. Thanksiwire said:Please explain how there are no conductors?
You can't go wrong with 3/0 Cu here :wink: ...although it *may* be possible to use 1/0 Cu.P.E.S. said:Inspector calling for #3/0cu, that seeems too big, but cannot find specifically in code to refute or agree with his call. Thanks!
P.E.S. said:I need help to size a water/gas bonding conductor on a 600 a service. There are no feeder conductors for me to know the size. Inspector calling for
#3/0cu, that seeems too big, but cannot find specifically in code to refute or agree with his call. Thanks!