I hope someone can help mewith this please. We recently built a 40Kw single phase generator set to backupa house. We used a 65Kw, 3-phase re-connectable alternator, connected it to doubledelta 120/240 volts. The rating sticker was marked as follows: 40Kw, 40Kva, 1.0Phase, 240 Volts, 1.0 Power Factor 167 Amps. We installed a 200 Amp CircuitBreaker.
The electrical inspector disagreed with the above. He stated that seeing thegenerator's original plate was marked at 50Kva, 0.8 power factor, the generatorcould NOT be rated at 1.0 power factor and therefore instructed that thebreaker be changed to reflect 40Kw Single phase, 240 volts at 0.8 power factor,which calculates to 208 Amps, so we were instructed to install a 225A CircuitBreaker. Is he correct or out to lunch?
The electrical inspector disagreed with the above. He stated that seeing thegenerator's original plate was marked at 50Kva, 0.8 power factor, the generatorcould NOT be rated at 1.0 power factor and therefore instructed that thebreaker be changed to reflect 40Kw Single phase, 240 volts at 0.8 power factor,which calculates to 208 Amps, so we were instructed to install a 225A CircuitBreaker. Is he correct or out to lunch?