I am pulling (3) 2/0, (1) 1/0, and a #4 through 2" conduit, how do I properly size a condulet "c" for pulling in the middle of the run? a standard 2" condulet "c" is marked (3) 3/0 max and 72.0 c.i.
infinity said:A C condulet needs to be sized for 8X the trade size of the raceway. Where the manufacturer lists the number and size of conductors within the condulet you may use that information for pulling purposes even if it's less than the 8X calculation. The Cu. In. area doesn't matter for pulling purposes.
nakulak said:then please explain 314.16 C (2005)