dudikr2
- New York, NY
Hey guys. I'm a young EE, and I'm trying to teach myself industrial motor controls from a textbook I bought, however there's no answer key and want to see if my answer is correct.
You are building a motor control cabinet that contains six motor starters and six pilot lamps. All control components operate on 120 volts AC. Two of the motor starters have coil currents of 0.1 amps each, and four of the motor starters have coil currents of 0.18 amps each. The six pilot lights are rated at 5 watts each. If the supply room has control transformers with the following ratings in volt-amperes (75, 100, 150, 250, 300, and 500), which transformer would you choose to supply power for all the control components?
So I added up all the currents:
(0.18 x 4) + (0.1 x 2) = 0.92 A
Then I used the formula I=(VA/E) but rearranged it so it was VA=I x E = (0.92 x 120) = 110.4 VA
I rounded this up to the next available size transformer, which is 150 VA.
The only trouble I have with this answer is that I didn't factor in the six pilot lamps at all. I don't see how I can factor them in since I don't have a power factor value to convert the watts to VA. So I'm thinking maybe they're irrelevant for sizing the transformer? Or maybe I just did the entire problem wrong. Any assistance would be appreciated.