I’m trying to size a 3ph 480V-480/277V transformer. Construction has already purchased a 4/W600kCMIL feeder (for the secondary to panelboard)
- using 310.16 the amps are 420 at 75 degC
So if I size the XFMR secondary to the conductors I’d get a 200kVA with 480V-480-277V
200000/277 x 1.732 = 417A
Is this correct?