Sizing a feeder for two or more motors?

Status
Not open for further replies.

ritelec

Senior Member
Location
Jersey
Hypothetical:

single phase 230 v motor. 2 hp 12a FLC

Circuit
conductor size x 1.25% = 15a = 14awg
short circuit and ground fault FLC x 250% = 30a

If I want to bring a feeder over for two and tap, what size feeder?

I remember 1.25% of largest plus the other. That would be a 12 x 1.25= 15a + 12a = 27a

I'm thinking a 40a feeder.

Where does this leave this feeder breaker at start up if they start at the same time.. ?

Thank you
 