Hello,
I have an Outside Air Rooftop Unit whose power specs are below.
Voltage: 208/60/3
FLA/MCA/MOCP: 24.3/28.8/45.0
I'm powering this unit from a main distribution panel.
The feeder number in the above picture is 8 that powers this unit.
I'm also providing a fused disconnect for this OARTU-1.
My question is, Will the breaker that protects feeder 8 be sized according to the ampacity of the conductor or according on the MOCP that is provided in the equipment (45).
my understanding is the breaker at feeder 8 should be speced to protect the ampacity of the conductor, and the fuse inside the equipment disconnect should be rated 45 amps to protect the equipment disconnect.
Thank you