In this application an 800HP DC drive is being fed from a Switchboard, in the SB is a 1600 LSIG Circuit Breaker and in the drive enclosure is a 1600 Amp Mag Trip Circuit Breaker.
4 runs of 500 MCM in 3? EMT conduits will service the drive enclosure.
When sizing the ground conductor I generally use table 250.122; in this case a copper ground would be at least a 2 AWG corresponding Ampacity of the current carrying conductors in each 3? conduit.
An engineer here mentioned using table 250.66 to size the grounding conductor; which in this case, would be 1/0.
Is table 250.122 the correct table to use in the application above?
When would table 250.66 be used? Perhaps, if a Switchboard was feeding an I-Line Panelboard?
4 runs of 500 MCM in 3? EMT conduits will service the drive enclosure.
When sizing the ground conductor I generally use table 250.122; in this case a copper ground would be at least a 2 AWG corresponding Ampacity of the current carrying conductors in each 3? conduit.
An engineer here mentioned using table 250.66 to size the grounding conductor; which in this case, would be 1/0.
Is table 250.122 the correct table to use in the application above?
When would table 250.66 be used? Perhaps, if a Switchboard was feeding an I-Line Panelboard?