jtester
Senior Member
- Location
- Las Cruces N.M.
I am trying to size a gutter for a service at a multi tenant building. I have two sets of underground service lateral conductors, each in 4? conduit, entering the gutter and 4 meters and service disconnects mounted under the gutter and being fed from them. One set of conductors feeds 3 meters and one set is pulled through the gutter and feeds one meter. This is similar to Exhibit 230.3 in the 2008 Handbook except there are two sets of underground service lateral conductors instead of 1 set of overhead.
Using 366.58 B for the set being pulled through the gutter, not the ones being tapped, I come up with over 30? of gutter height. This seems incredible, what am I doing wrong?
I know some of you will suggest that I don?t run the untapped set thru the gutter, but our local utility believes that one point of service means one enclosure, and they will not allow the conductors to enter two separate enclosures.
Thanks in advance for any help.
Jim T
Using 366.58 B for the set being pulled through the gutter, not the ones being tapped, I come up with over 30? of gutter height. This seems incredible, what am I doing wrong?
I know some of you will suggest that I don?t run the untapped set thru the gutter, but our local utility believes that one point of service means one enclosure, and they will not allow the conductors to enter two separate enclosures.
Thanks in advance for any help.
Jim T