Thanks
Thanks
Thank you both for your help. Augie47 you are probably right about the depth. My thinking was ... I have two rows of six conduit entering the back side up high, and two rows exiting as far forward out the bottom, keeping eight inches separation for the heat calcs; that puts my constraint at the distance between the lower row entering the back and the back row exiting the bottom. My first thought was to use an eighteen inch deep box. Doing so would give me nine inches from center of the bottom conduit and the back wall. If I used 312.6a correctly I should need eight inches minimum. If I used the closest edge of the four inch conduit and not the center of it I would be less than eight inches, so that was why I did opt for the 24. Is this thinking in error?