MattWilliams
- Minnesota
- Instructor
Say I have 3-phase commercial service that has a calculated maximum load of 685 amps after all correction and adjustment factors have been applied, as well as all 125% continuous load factors added in. I’m using 3 conductors per phase for service conductors, and I choose 4/0 Xhhw-2 copper conductors for a total ampacity of 690 Amps(230A x 3 conductors per phase).
Is it accurate that I may use the provisions of 240.4(B) to provide the Main fuse/breaker protection and go to the next higher standard size of 700 Amps?
It appears that a great deal of commercial calculations has their conductor ampacity exceeding their main fuse/breaker size even though they technically should not have to. I know there is nothing wrong with having a higher conductor ampacity but from a code standpoint, I don’t see anything wrong with having my breaker size exceed my wire ampacity as long I don’t go past another fuse/breaker size or exceed 800 amps.
Is there a code article that supersedes my ability to go to the next standard size or should my service conductor ampacity always match or exceed my fuse/breaker size?