cavejumper
Member
- Location
- Ohio
Hi everyone! Thank you all for your assistance, both now and in the past, and for being a great resource to myself and the entire electrical industry! I've certainly learned a lot reading through the forums, and if I have a question on anything, this is one of the first places I'll look for an answer.
As the title says, I'm doing calculations to size a step-up transformer and feeder for a dedicated motor load, and I want to make sure I'm doing it properly. My customer is on a budget, so I don't want to oversize it, but I want to make sure it'll work for him as well. I looked at other threads relating to this, and I think I got it, but I would like more knowledgeable people to look at this too and make corrections or suggestions as necessary. So here we go:
The equipment is an air compressor with a 75HP, 460V motor. The manufacturer says FLC is 105.5A, LRC is 479A. I have not see it, and I have no other info on it other than the manufacturer says there is no duty cycle listed. I'm under the impression that it doesn't have any variable speed drive or soft start or anything like that.
The building has a 240V delta service with enough capacity to handle this, but I would need to install a step-up transformer to do so. This transformer would be dedicated to this equipment (which does not need a neutral). Should I be looking for a 240V delta - 480V wye transformer, or would another configuration be better?
I've sized my motor feeder (480V) as follows:
Conductor ampacity (125% of FLC) - 131.9A
Overload protection rating (140% of FLC) - 140A
Short circuit protection rating (150% of FLC) - 175A
Here's where I'm uncertain - I'm not sure what number to use to size the transformer. If I go with 125% of FLC of the motor -> 105.5x1.25=131.9A -> 131.9Ax480Vx1.732=109.6KVA -> I would use a 112.5KVA transformer. Is this adequate?
Assuming it is, and I continue my calculations, my transformer rated current will be -> 112500VA/(240Vx1.732)=270.6A. Then my conductor ampacity will be -> 270.6Ax1.25=338.3A, and my overcurrent protection will be 350A.
I don't know how much voltage drop would be acceptable for this motor. I also don't know how much impendance there'll be in the system, but I can say that the compressor will be located close to the gear feeding it - I'll probably only have about 50-70' of conductor between the primary OCPD and the motor.
Please look over my figures and let me know if I need to change anything. Thanks for your help!
As the title says, I'm doing calculations to size a step-up transformer and feeder for a dedicated motor load, and I want to make sure I'm doing it properly. My customer is on a budget, so I don't want to oversize it, but I want to make sure it'll work for him as well. I looked at other threads relating to this, and I think I got it, but I would like more knowledgeable people to look at this too and make corrections or suggestions as necessary. So here we go:
The equipment is an air compressor with a 75HP, 460V motor. The manufacturer says FLC is 105.5A, LRC is 479A. I have not see it, and I have no other info on it other than the manufacturer says there is no duty cycle listed. I'm under the impression that it doesn't have any variable speed drive or soft start or anything like that.
The building has a 240V delta service with enough capacity to handle this, but I would need to install a step-up transformer to do so. This transformer would be dedicated to this equipment (which does not need a neutral). Should I be looking for a 240V delta - 480V wye transformer, or would another configuration be better?
I've sized my motor feeder (480V) as follows:
Conductor ampacity (125% of FLC) - 131.9A
Overload protection rating (140% of FLC) - 140A
Short circuit protection rating (150% of FLC) - 175A
Here's where I'm uncertain - I'm not sure what number to use to size the transformer. If I go with 125% of FLC of the motor -> 105.5x1.25=131.9A -> 131.9Ax480Vx1.732=109.6KVA -> I would use a 112.5KVA transformer. Is this adequate?
Assuming it is, and I continue my calculations, my transformer rated current will be -> 112500VA/(240Vx1.732)=270.6A. Then my conductor ampacity will be -> 270.6Ax1.25=338.3A, and my overcurrent protection will be 350A.
I don't know how much voltage drop would be acceptable for this motor. I also don't know how much impendance there'll be in the system, but I can say that the compressor will be located close to the gear feeding it - I'll probably only have about 50-70' of conductor between the primary OCPD and the motor.
Please look over my figures and let me know if I need to change anything. Thanks for your help!