Sizing a Utility Transformer for PV and Building Load

Status
Not open for further replies.

baserunner4

Member
Location
CA
Hello,

Say I have a 2 building loads of 208Y/120A at 400amps. The transformer cans are 3 50KVA at 208Y/120V. I want to interconnect at the splice blocks the secondary side of the transformer so it will offset both mains and their respective meters. I'll be using inverters that have a 40A max. Can I size up to 320A or 400A for the solar? Is there anything else that I should be careful of? I will be seeking out to a professional just trying to get a heads up before I approach them.

Thanks
 
Hello,
... I want to interconnect at the splice blocks the secondary side of the transformer so it will offset both mains and their respective meters. ...

:blink:
What does that mean? Where are the meters? You cannot backfeed two meters with one solar system. What is the metering regime for this solar system?

Other than that, if you have a supply side connection and a 400A service then you could backfeed 320A nameplate inverter current, yes.
 
:blink:
What does that mean? Where are the meters? You cannot backfeed two meters with one solar system. What is the metering regime for this solar system?

Other than that, if you have a supply side connection and a 400A service then you could backfeed 320A nameplate inverter current, yes.


I didn’t think of that. I think it would be a new service. The current meters are after the main circuit breakers.
 
Hello,

Say I have a 2 building loads of 208Y/120A at 400amps. The transformer cans are 3 50KVA at 208Y/120V. I want to interconnect at the splice blocks the secondary side of the transformer so it will offset both mains and their respective meters. I'll be using inverters that have a 40A max. Can I size up to 320A or 400A for the solar? Is there anything else that I should be careful of? I will be seeking out to a professional just trying to get a heads up before I approach them.

Thanks

400A OCPD and 320A inverter output. NEC 705.12(A), "The sum of the ratings of all overcurrent devices connected to power production sources shall not exceed the rating of the service." The utility will have to allow virtual net metering for this to offset the meters.
 
I should say one more thing on this subject. Utilities rate things differently then we do based on the NEC. So while the distribution transformer might have a nameplate rating of 150kVA and the utility owned conductors might be rated for 400A by the NEC the utility might not rate this as a 400A service. Get the service rating from the utility and use that to base the back feed on.
 