Mike Lang
- New Jersey
I'm looking at a job where I need to supply 480 volts for a pump 10 Horsepower and the building has a 120 / 208 3 phase WYE. Can you guys double check my calculations so I know im on the right page.
The new pump operates at 480 volts 3 phase and FLA is 16.1.
To figure out the size of the WYE Delta transformer I did 480 x 16.1 x 1.732 = 13385 VA or 13.3kVA The next available transformer is a 15 kVA.
My primary side OC protection would be 60 Amps. 15000 VA divided by 360(208 x 1.732) = 41.666 Since it's over 9 amps I multiply by 125% = 52.08 Amps next higest size = 60 amp breaker on primary.
I bet someone asks why I don't just order a 120 / 208 3 phase pump at 10 horsepower.