I have always used no. 2 Al for 100 amp and 4-0 for 200 amp these are basically all that is available at supply houses around here. I am talking overhead here acsr. Would this be wrong for anything but residential.
A #2 Al conductor in open air cannot carry 100A as a general rule. It can be used for a 100A nominal load only when it carries the entire load of a residential occupancy. Use as a feeder carrying part of the load or any use other than residential does not permit a nominal load of 100A.I have always used no. 2 Al for 100 amp and 4-0 for 200 amp these are basically all that is available at supply houses around here. I am talking overhead here acsr. Would this be wrong for anything but residential.
#2 AL is only good for 90A on the seventy five degrees C column, and you will have to go on the journey of a lifetime to find a breaker or fuse that is has terminals marked for anything higher, so you are stuck using 90A over current protection for anything other than a resi service, (TABLE 310.15(B) (7)) and that's all there is to it.They are hanging in air and not terminated on any terminals so what could be derated?
A #2 Al conductor in open air cannot carry 100A as a general rule. It can be used for a 100A nominal load only when it carries the entire load of a residential occupancy.
Actually, if it is used as an overhead service drop and connected to other conductors at the weather-head, you only need to find a split bolt or butt splice rated for 90 degrees.#2 AL is only good for 90A on the seventy five degrees C column, and you will have to go on the journey of a lifetime to find a breaker or fuse that is has terminals marked for anything higher,
If you are talking about the quadplex overhead messenger wire, the free-air ampacity in table 310.15(B)(17) applies. #2 THHW 75° AL in free air is rated at 135 A. Ampacities take a big jump when there is no raceway.
If you are talking about the quadplex overhead messenger wire, the free-air ampacity in table 310.15(B)(17) applies. #2 THHW 75° AL in free air is rated at 135 A. Ampacities take a big jump when there is no raceway.
Then again, it's max attainable circuit ampacity when under NEC purvue is still going to be regulated by Table 310.15(B)(16) because of 110.14(C) limitations.That is a very valid point. Folks get used to looking at 310.15(B)(16) and forget the limitations on that Table.
It is pretty much ignored by inspectors but you might want to keep in mind utility type ACSR (triplex) is not even a NEC recognized conductor and is not listed in any Table.
#2 utilit ASCR is nicknamed "shrimp" an with a XLP insulation has an ampacity of 150 amps (based on 40°)
(see here: http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet34)
When you add all the facts together you can see why most inspectors care less about "triplex" as long as it's in free air.
edit: above info was triplex
#2 quadraplex is Belgin or Mustang and 135 amps see here: http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet35