1) I have a 1200A 208V 3p 4w fused disconnect and meter for a restaurant in the electrical room in the basement of a shopping center.
2) I have 4ea 4"PVC conduits leaving the disconnect carrying 4ea 500MCM + 1ea 250MCM traveling approximately 60' to the restaurants electrical closet. For a total of 16ea 500MCM and 4ea 250MCM conductors.
3) These conduits and conductors go thru the floor into the bottom of gutter that is 16"X16"X48". The conduits are entering in a straight line at the back of the gutter on one end. The conductors will be terminated under 5 splice blocks staggered along the 48" gutter.
4) The tenant will install 4ea 400A MB panelboards and will connect those to the gutter with his own conduits all within about 15' of the gutter. The conductors will tap onto the parallel service at the tap blocks.
or
The tenant will set a 1200A MDP on top of the gutter and feed it thru 4 conduits of his and his conductors.
What sized do I need to change the 16"X16"X48" gutter to for it to meet code?
2) I have 4ea 4"PVC conduits leaving the disconnect carrying 4ea 500MCM + 1ea 250MCM traveling approximately 60' to the restaurants electrical closet. For a total of 16ea 500MCM and 4ea 250MCM conductors.
3) These conduits and conductors go thru the floor into the bottom of gutter that is 16"X16"X48". The conduits are entering in a straight line at the back of the gutter on one end. The conductors will be terminated under 5 splice blocks staggered along the 48" gutter.
4) The tenant will install 4ea 400A MB panelboards and will connect those to the gutter with his own conduits all within about 15' of the gutter. The conductors will tap onto the parallel service at the tap blocks.
or
The tenant will set a 1200A MDP on top of the gutter and feed it thru 4 conduits of his and his conductors.
What sized do I need to change the 16"X16"X48" gutter to for it to meet code?