we have a situation where a brand new building is a 208/120V service, but someone goof'd and ordered 460V RTU's...the RTU manufacturer is asking us to look at solutions that don't involve replacing all the RTU's (which are already on the roof and installed)....
One possible solution is to install a transformer and step up to 480V for a panel to feed the unit. There are 6 units total. 1-15T, 4-8.5T and 1-6.5T. If my memory is correct, I need to size the panel as follows:
300% of the largest RLA plus the RLA of the other loads. In this case the RLA of the 15T is 42.6A, the 8.5T are 28.2A and the 6.5T is 19.6A (all at 480V)
(42.6x3) + (28.2x4) + 19.6 = 260A @ 480V...
is it this simple?