Sizing bonding jumper
Looks like this is for a service so the bonding jumper is based on the size of the conductors in each individual raceway when using individual bonding jumpers. For 500 kcmil aluminum the bonding jumper is a minimum of #2 copper or #1/0 aluminum according to Table 250.102(C)(1).
For a single bonding jumper for all three raceways you would use 12.5% of the 3 sets combined or 500 kcmil*3*12.5%.
so in your opinion is my interpretation of the 250.102 (C) (2) (1) correct ?
No opinion. The minimum size for individual copper bonding jumpers for each raceway is in fact #2 copper but based on the answers #2/0 would be code compliant. I find the use of the term bonding jumper to be somewhat lazy. Since this is learning material the correct term Supply Side Bonding Jumper (SSBJ) should be used.
The question is misleading. They all work. The minimum size per raceway is #2 and 2/0 when bonding all of the raceways with one supply side bonding jumper.
I agree. The question and the graphic do not match. Looks like a mistake to me.
For Al, 12.5% only applies over 1750 kcmil. For 1500 kcmil the table gives 2/0.
Agree that the answers provided seem to be based on all 3 sets in one raceway, while the diagram shows one set per raceway.
Cheers, Wayne
Cheers, Wayne
You're correct. I should have looked before answering. T250.102(C)(1) ends at 1100 kcmil for copper not aluminum.