If you have a raceway say EMT with an EGC that is terminated to a ground bus, if a bonding jumper is not required but installed anyway is it required to be sized properly?  The EGC in this case is 350 kcmil but the largest terminal on a bonding bushing is only 250 kcmil so a 250 bonding jumper was installed.
	
		
			
		
		
	
				
			
			