Sizing Branch Circuits

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
If your feeding receptacles I assume it depends what’s plugged into it(contin load or not) to determine whether or not it should be sized at 125%?
 
IMO, If the circuit is for a specific load you size the circuit for that load (100% non continuous 125% continuous ) then size the receptacle based on that branch circuit size.
 
I think there is a difference between the bare minimum the code requires and what makes sense too. If I had a bunch of appliances that I knew were going to be regularly used, possible simultaneously, I would want more circuits even though code might let me get by with fewer.
 