we build machines where i work and the ee are driving me nuts about the size of breaker and wire i say they need, i need your help.
the machine has heaters and a laser and small servo motors.
feed is 208 3p 4w---- not balanced the heaters are 120 volt so the neut. has current from the heaters. the machine will run 24/7.
questions: this would be a cont.load because it runs more then three hours, correct? even if its not at full load?
i would reduce the breaker rating too 80% right?and base the size on the full load amp rating even if it doesn't draw that all the time?
the conductor rating would be times 1.25 because of the cont. load correct?
thanks
kurt