Sparky1981
PE
- Location
- Denver, CO
- Occupation
- Electrical/Lighting Engineer
As of recent Denver has been bringing this up in our reviews. I am wondering how you all size the breaker feeding a motor. In the mechanical schedule we get
FLA: 177A
MOCP:200A
To size the wire I take 177A*1.25=221.3A, so I use #4/o copper
To size the breaker out of my gear I use table 430.52, Inverse time breaker.
177A*2.5=442A.
I typically will size down and in this case I used 300A.
So I now have a 300A breaker, #4/O copper wire feeding this unit.
We got rejected because the reviewer says the mechanical schedule calls out for a MOCP of 200A. With a full load of 177A I feel like I am asking for trouble sizing my breaker that close to the FLA. Further I would assume the unit would be provided with overcurrent of 200A protecting my wire. Perhaps the reviewers are seeing a 300A breaker with 230A wire and having heart burn.
Would you provide the 200A breaker mechanical asks for? Or how do you go about sizing this stuff?
Again for years, review after review, this has never been brought up. But on the past two projects it has. So I am now baffled.
FLA: 177A
MOCP:200A
To size the wire I take 177A*1.25=221.3A, so I use #4/o copper
To size the breaker out of my gear I use table 430.52, Inverse time breaker.
177A*2.5=442A.
I typically will size down and in this case I used 300A.
So I now have a 300A breaker, #4/O copper wire feeding this unit.
We got rejected because the reviewer says the mechanical schedule calls out for a MOCP of 200A. With a full load of 177A I feel like I am asking for trouble sizing my breaker that close to the FLA. Further I would assume the unit would be provided with overcurrent of 200A protecting my wire. Perhaps the reviewers are seeing a 300A breaker with 230A wire and having heart burn.
Would you provide the 200A breaker mechanical asks for? Or how do you go about sizing this stuff?
Again for years, review after review, this has never been brought up. But on the past two projects it has. So I am now baffled.