Hello all. I have a 10hp, 208/3 ph motor.
Using Table 430.250, we have FLC of 30.8A.
I am trying to size the breaker for this motor. Using Table 430.52, for OCP calculation:
30.8A*1.75 = 53.9A.
Now, T430.52/430.52(C)(1) says this is the maximum rating or setting, implying I would select the next size down, or a 50A breaker.
But 430.52(C)(1) Exception No.1 permits (no verbiage indicating it requires) us to use the next higher standard ampere size if the value determined in the above calculation doesn’t correspond to a standard size. This leads me to a 60A breaker.
Is this exception “mandatory”. In other words, do I select the 60A breaker because and only because 53.9A is not a standard size? Or is this exception there simply for design choices/flexibility.
Thank you in advance for your time.