See attached pictures of data from elevator shop drawings, motor table shows 60R (drive HP) - 20A running amp., AC Motor Parameter Set Up table shows 60R equals 60HP. If going with 60HP, per NEC table, motor FLA = 77A. Should I size breaker to protect this elevator based on 60R or 60HP - full load amp.? This is a huge amp. draw difference so as breaker size (if using 2.5 x motor FLA rule). I never heard of drive HP term before. Data sheet does not have information for recommended breaker for fuse protection. Thank you.