slc410
Electrician
- Location
- Madison wi
- Occupation
- Electrician
Im trying to size my bond to building steel for a 400 amp sevice. From the meter the service conductors enter the building in parallel sets of 3 phase 3/0. Each set going to their own main breaker 200 amp panel. My thinking is that the wire should be a 1/0 to building steel since it is a parallel set, three 3/0 ungrounded conductors is equivalent to a 600 kcmil. 250.66 then tells me 1/0 to both panels (not allowed to bond in meter)