Isaiah
Senior Member
- Location
- Baton Rouge
- Occupation
- Electrical Inspector
I have a 300A CB at an indoor SWGR feeding a 3ph load of 270A located outdoors. I want to use 350kCMIL cable.
I used the 90 degree C column for ambient correction of Table 310.15(B)(2)(a) at 36-40C (i.e. 350A x 91=318.5A) for the outdoor run in rigid galvanized steel conduit.
The switchgear resides in a climate controlled environment so I’m assuming the 310A doesn’t require ambient correction since the CB/lugs are in a cool environment. At the lugs, you’d have 310A per the 75 degree C column in 310.15(B)(16) of the 2017 NEC.
Is this correct?
Sent from my iPhone using Tapatalk
I used the 90 degree C column for ambient correction of Table 310.15(B)(2)(a) at 36-40C (i.e. 350A x 91=318.5A) for the outdoor run in rigid galvanized steel conduit.
The switchgear resides in a climate controlled environment so I’m assuming the 310A doesn’t require ambient correction since the CB/lugs are in a cool environment. At the lugs, you’d have 310A per the 75 degree C column in 310.15(B)(16) of the 2017 NEC.
Is this correct?