I have a client with an existing 480V, 3 ph, 600A MCC, fed from an existing 600A (80% rated) breaker in a remote panel, using 2 x 350 Kcmil (2 x 310A = 620A) sets. The existing MCC is Main Lug Only (No main breaker). The largest motor is 75 HP.
I want to add a couple of MCC sections, but I think I may need more power than the code will allow.
Normally, when I've sized an MCC, I take the largest motor FLA x 1.25 then add the sum of the other motor FLAs. (per 430.24)
When I do this I get 584 Amps.
(464A + 1.25 x 96A = 584)
So I believe that my MCC is properly sized. All good right?
But when I check the MCC feeder sizing, I run into some confusion. (I assume the conductors feeding the MCC are "feeders", no?)
Article 215.2 (A)(1) feeder sizing, says two things:
First, use article 220, (I find 220.50, which sends me back to 430.24) which is all good.
Second, use 100% of non-continuous loads + 125% of continuous loads. Here I have a problem. Since my loads are all continuous I get:
(464 + 96) x 1.25 = 700A Uh-Oh.
It looks to me like the normal MCC sizing procedure in 430.24 will almost never apply to the sorts of industrial projects (continuous HVAC loads & Process loads) I typically encounter. I'll be needing to size the feeder first, because the requirements are more stringent, and then make the MCC match.
Is this so?
Am I doing these calcs correctly? Am I overlooking anything?
The kicker is that I know when the system is all running, it'll be drawing something on the order of 400 Amps. The bigger motors are on VFDs, the break horsepowers are probably less than 85%, the typical operating diversity for these facilities is around 70%. I can confidently say that this MCC will never see more than 450 Amps. But I don't have a month or a year's worth of data as required by 220.87.
I'd prefer not to put in a new feeder to a new MCC for this application, but my understanding is that the AHJ is rather strict in this location.
Any advice?
Thanks in advance,
Dave
I want to add a couple of MCC sections, but I think I may need more power than the code will allow.
Normally, when I've sized an MCC, I take the largest motor FLA x 1.25 then add the sum of the other motor FLAs. (per 430.24)
When I do this I get 584 Amps.
(464A + 1.25 x 96A = 584)
So I believe that my MCC is properly sized. All good right?
But when I check the MCC feeder sizing, I run into some confusion. (I assume the conductors feeding the MCC are "feeders", no?)
Article 215.2 (A)(1) feeder sizing, says two things:
First, use article 220, (I find 220.50, which sends me back to 430.24) which is all good.
Second, use 100% of non-continuous loads + 125% of continuous loads. Here I have a problem. Since my loads are all continuous I get:
(464 + 96) x 1.25 = 700A Uh-Oh.
It looks to me like the normal MCC sizing procedure in 430.24 will almost never apply to the sorts of industrial projects (continuous HVAC loads & Process loads) I typically encounter. I'll be needing to size the feeder first, because the requirements are more stringent, and then make the MCC match.
Is this so?
Am I doing these calcs correctly? Am I overlooking anything?
The kicker is that I know when the system is all running, it'll be drawing something on the order of 400 Amps. The bigger motors are on VFDs, the break horsepowers are probably less than 85%, the typical operating diversity for these facilities is around 70%. I can confidently say that this MCC will never see more than 450 Amps. But I don't have a month or a year's worth of data as required by 220.87.
I'd prefer not to put in a new feeder to a new MCC for this application, but my understanding is that the AHJ is rather strict in this location.
Any advice?