Hi I'm working on a project in Central Florida and I have an engineer confusing me.
The code (Article 110-3) states that systems must be installed as listed or labeled and we have an RTU with a name plate that specifically states that the maximum circuit breader size is to be 35 amps.
The engineer has put this RTU on a 70 amp breaker and requires us to use number 4 conductors for a short run. Does this make any sense to anyone?
Same engineer requires us to use a number 2 for a 50 amp RTU on a 100 foot pull.
Same engineer selects Brown, Orange and Yellow conductors for both high and low voltage applications and Black, Red and Blue for both high and low voltage applications when the code (article 240) requires that all systems and phases be coded.
The code (Article 110-3) states that systems must be installed as listed or labeled and we have an RTU with a name plate that specifically states that the maximum circuit breader size is to be 35 amps.
The engineer has put this RTU on a 70 amp breaker and requires us to use number 4 conductors for a short run. Does this make any sense to anyone?
Same engineer requires us to use a number 2 for a 50 amp RTU on a 100 foot pull.
Same engineer selects Brown, Orange and Yellow conductors for both high and low voltage applications and Black, Red and Blue for both high and low voltage applications when the code (article 240) requires that all systems and phases be coded.