I'd like to apologize in advance if this is a redundant question (I've searched and found similar questions but they have also left me confused).
I have a Trane Chiller that has 4 compressors at RLA=18.6A each. It also has 4 fans at a total FLA=12.6A. It also has some controls, but it doesn't specify the power.
The unit states the MCA=93A and the MOP=110A. I've seen countless ways to get to the MCA and MOP based on the compressor and fan information provided above, but I'd like a clearer answer based off of my specifics if at all possible.
Also, I'm having a little confusion with section 440 of the NEC stating that the breaker should be sized at 125% of the load, or kept at 80% breaker capacity. Is this a calculation that is built into the MCA and MOP?
Long story short, is it acceptable to utilize a 100A breaker for this chiller and not be in violation of the chiller specs or code?
Thanks