subinstaller
Member
Hello all, hope I can get some advice on sizing circuit breaker and power conductors in a DC power application (specialized telecom application, -54 volts normal operating voltage, -40.5 volts minimum operatiing voltage).
The equipment I'm trying to size the cb and conductors for has a maximum power input of 700 amps DC (at -40.5 volts). But under normal system operating conditions, the equipment will not consume more than 400 amps DC (at -40.5V). So 400 amps is the expected load, the only way the equipment would require the 700 amps would be if some technican inadvertanly went into the system parameters and changed things, there is no mechanical or software safe guards to prevent this from happening. The operating procedures are written to keep the system at a level where it will only need 400 amps DC input, but again, aside from written procedures and training, a technican would be physically able to ramp things up where the equipment would consume the 700 amps input.
So my question to the forum is.................based on NEC, do I need to size my circuit breaker and power cabling based on the 700 amps the equipment is capable of consuming or the 400 amps that it will normally be operatiing at?
Any advice, especially pointing to NEC section(s) would be appriciated. (I realize most outages are caused by human error so not looking for that type of input, really need to understand the code for this situation)
Thank you
The equipment I'm trying to size the cb and conductors for has a maximum power input of 700 amps DC (at -40.5 volts). But under normal system operating conditions, the equipment will not consume more than 400 amps DC (at -40.5V). So 400 amps is the expected load, the only way the equipment would require the 700 amps would be if some technican inadvertanly went into the system parameters and changed things, there is no mechanical or software safe guards to prevent this from happening. The operating procedures are written to keep the system at a level where it will only need 400 amps DC input, but again, aside from written procedures and training, a technican would be physically able to ramp things up where the equipment would consume the 700 amps input.