SIZING COLD WATER CONDUCTER

Status
Not open for further replies.

Keldra

Member
Location
FORT WORTH, TX
I AM TRYING TO SIZE THE COLD WATER CONDUCTER FOR A 300 AMP SERVICE ON A RESIDENTIAL TRIPLEX COULD I GET SOME SUGGESTIONS ON WHERE TO FIND INFO , OR WHAT SIZE I WOULD NEED THX
 
Last edited:
I AM TRYING TO SIZE THE COLD WATER CONDUCTER FOR A 300 AMP SERVICE ON A RESIDENTIAL TRIPLEX COULD I GET SOME SUGGESTIONS ON WHERE TO FIND INFO , OR WHAT SIZE I WOULD NEED THX

The installation of Grounding Electrode Conductors are specified in the NEC starting at 250.52 and continues through and including 250.70. The size of the GEC is determined by the size of the service conductors per 250.66 and the associated table and notes.

Please don't yell. ( Typing in all caps is considered yelling. )
 
The installation of Grounding Electrode Conductors are specified in the NEC starting at 250.52 and continues through and including 250.70. The size of the GEC is determined by the size of the service conductors per 250.66 and the associated table and notes.

Please don't yell. ( Typing in all caps is considered yelling. )
Hmmmmm..maybe they are yelling...lol
 