G garyfitzgerald Member Dec 4, 2006 #1 Specs for a large chiller are MCA=382, MOCP=600. Do I size the feeders to the MCA or the MOCP?
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Dec 4, 2006 #2 garyfitzgerald said: Specs for a large chiller are MCA=382, MOCP=600. Do I size the feeders to the MCA or the MOCP? Click to expand... The former, as long as the unit contains its own overload protection.
garyfitzgerald said: Specs for a large chiller are MCA=382, MOCP=600. Do I size the feeders to the MCA or the MOCP? Click to expand... The former, as long as the unit contains its own overload protection.
iwire Moderator Staff member Location Massachusetts Dec 4, 2006 #3 garyfitzgerald said: Do I size the feeders to the MCA or the MOCP? Click to expand... I agree with Larry, you certainly can size the conductors per MCA. However you may want to consider voltage drop at start up.
garyfitzgerald said: Do I size the feeders to the MCA or the MOCP? Click to expand... I agree with Larry, you certainly can size the conductors per MCA. However you may want to consider voltage drop at start up.