Btw...they are running 3/0 Al wire. Seems way oversized although the run is 300'.
Btw...they are running 3/0 Al wire. Seems way oversized although the run is 300'.
using southwire calc
3 ph 208
al
conduit
3% drop
300'
80 a
3/0 2.7%
~ the same by hand
I did too, first timeFor some reason I decided to use copper in my calc's. :slaphead:
More precisely, you choose the trip setting based on the ampacity of the conductors, after you have chosen the ampacity value based on the calculated load. But yes, you are right.