Sizing Conductor For Breaker
mstrlucky74
NJ
In picture attached the 225AF is frame size but you would size wire to the trip which is 80A, correct? Thanks.
charlie b
Lockport, IL
Semi-Retired Electrical Engineer
More precisely, you choose the trip setting based on the ampacity of the conductors, after you have chosen the ampacity value based on the calculated load. But yes, you are right.
infinity
New Jersey
Journeyman Electrician
Btw...they are running 3/0 Al wire. Seems way oversized although the run is 300'.
Way oversized. According to my VD calculator using maximum values (300', 80 amps) for 208 volts the minimum conductor size for less than 3% VD is #1 AWG, for 480 volts it's #3 AWG.