Sizing conductors-100a or less

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Watchung MH 2005 dvd's. Do you still use the 60 degree column for sizing conductors 100amps or less regaedless if the terminals are rated higher? Thanks

Edit: juat saw the part of video that says you can use higher column if terminals are rated for it
 
Last edited:
That's correct. You have to size to the weakest link. If the terminals are not marked then you must assume 60C for 100 amps or less.
 