Sizing conductors 100a or less

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
So if the equipment is not marked you are to use the 60 degree Column or it could be marked 75 degree then that column would be used. How often is equipment 100a or less not marked or only marked 60 degree? I think just about all breakers are marked 75 degree. Thanks.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
As I recall, some devices 50 amps and less are 60° but the 240.4(D) restriction pretty much takes care of the problem,
 