Hi there, I've searched the forum for years as I've needed but just joined today. I've got a few runs of wire i would like some input on sizing. I'm self taught so anxious to learn any time i can.
Run 1
300 hp motor, according to my chart it should be 361 fla, but the manufacturer book calls for 458. Equipment is still in asia.
180 feet run. Equipment will run at roughly 60% load for 50 out of 60 minutes for 8 hours a day.
I'm coming up with 2 runs out 4/0 copper with #1 ground for each run calculated at 75 degrees.
Run 2
300 hp motor, same fla discrepancy.
280 foot run
This unit will run at 90% roughly 3 to 5 hours a day. I'm showing 4/0 is still okay but borderline so i thought id do 2 runs of 250 mcm to be safe, because of the fla discepancy and continuous load.
What are your thoughts and reasoning behind it?
Run 1
300 hp motor, according to my chart it should be 361 fla, but the manufacturer book calls for 458. Equipment is still in asia.
180 feet run. Equipment will run at roughly 60% load for 50 out of 60 minutes for 8 hours a day.
I'm coming up with 2 runs out 4/0 copper with #1 ground for each run calculated at 75 degrees.
Run 2
300 hp motor, same fla discrepancy.
280 foot run
This unit will run at 90% roughly 3 to 5 hours a day. I'm showing 4/0 is still okay but borderline so i thought id do 2 runs of 250 mcm to be safe, because of the fla discepancy and continuous load.
What are your thoughts and reasoning behind it?