What is the minimum size Type XHHW conductor that's permitted to terminate on a transformer protected on the primary side with a 50 A breaker if the circuit breaker and equipment terminals are listed for 75°C conductor sizing? Answer: 8 AWG copper wire.
▫ Comment_1: Seems to me that no math is required since conductors should not be sized at 125% of the fuse size; instead, the fuse size should be sized at 125% of the continuous load on the circuit, which means the conductor should be sized to handle that calculated load, not the other way around.
▫ Comment_1: In the past, I would have used the 125% rule and calculated 50 x 1.25 = 62.5 A, and therefore oversized the wire to 6 AWG copper wire.
Any insite per the NEC would minimum requirement for this conductor is appreciated.